hello william,
good to hear you have solved the problem.
out of curiosity and for future reference for those searching the forum topics with a similar question, can we review your configuration?
does this sound right?
-genset ground and neutral bond broken @ generator.
-240 ac out from a 2pole 50a breaker.
-L1 of output to designated master inverter.
-L2 of output to designated slave inverter.
-master inverter ground and neutral bonded with jumper.
-slave inverter ground and neutral with no jumper.
-genset ground to system ground?
-no neutral from genset?
thanks for the update and any added info for future reference.
best regards,
#1no knowledge, bec. my solar installer configured system with previous genset.
#2 either 120 or 240 for loads up to 12KW and surge to 15KW
both inverters show charge yellow light on when genset running at max. will not charge with genset in slow rpm and shows a red flashing light.
with no substantial house load, eg pool pump, well pump, washer, 1.5 kw water heater...19 gal., genset will start to vary speed and sound ever so slightly, once the load is removed.
the rest, see #1;
I can see I have a lot of learning to do. Wish I knew more about it.
We are starting our annual winter rains in So. AZ just now so am using genset more often now to keep batts above 80 percent charge due to extreme cloud cover. Yesterday at peak solar gen. time, system would only gen. 500 watts...this is from a 3.6kw solar system.
They are forecasting an inch of rain here so at least my panels will get a good washing. Dust cover on panels will impede the solar gen. up to 50% in my 4 years experience on solar only.