I was assuming that you were going to go up to 24 volts on the battery also. I would go to a 24 volt battery bank. Just series two 12 volt batteries. This accomplishes two things. It makes the draw on the batteries half as much which will make the batteries last substantially longer and it gives you more reserve power. The point I was trying to make on the charging was to have high enough volts at load out of the panel to maintain the batteries properly. To maintain the batteries properly you should be able to do a bulk charge at 2.37 to 2.45 volts per cell or 28.9 volts to recharge the battery. When the battery is fully charged you will want to fall back to a float charge of 2.2 to 2.23 volts per cell or 26.58 volts. Then on a regular basis several times a year you will need to do an equalization charge on the batteries at 2.58 to 2.67 volts per cell or about 31.5 volts. This prevents sulfation of the batteries and makes them last much longer.
Most charge controllers have these features built in and you just program the voltages, durations and how often the charge occurs. So for a 24 volt battery bank you will want a panel that is capable of doing an equalization charge to the batteries. Check the manufacturers charging recommendations for the specific batteries that you buy. The panel that you are looking at looks like a good choice to me. The Sharp panel will give you 35.86 volts at load so you should never have any trouble getting the voltage necessary to maintain a 24 volt battery bank and you will get efficient usage of the panel.
Regard,
Dennis