Hello again Conrad -
The sizing for the Shurflo above ground pumps can be a little tricky. I'll mention a few words about that before I get to the case of the Kaneka solar panels.
When you look at the chart for one of the Shurflo pumps, the quick and sure way to determine the number of watts required is to multiply the volts of the pump by the highest number of amps the pump could consume. For example, have a look at this pump:
http://www.altestore.com/store/Solar-Water-Pumps/Surface-Pumps/Shurflo-Surface-Pumps/Shurflo-2088-443-144-12V-Std-Surface-Pump/p1088/ According to the chart for that pump, the maximum current draw would be about 9.1 amps. So the 12V version, X 9.1, = 109.2 watts. But you don't want to go looking for a 109 watt panel. First, they don't exist. Second, the watt rating of a given solar panel is the NOMINAL watt rating. For the actual power of a solar panel - in other words, what the panel will operate at in the real world, subtract 20% of the nominal watt rating. Or add 20% to the size pump you are thinking about. In the case of the pump noted above, 109.2 X 1.2 (for 120%) = 131.04 watts. So you need a solar panel at least 131 watts. How much larger than 131 watts can you go? As long as the voltage of the panel or array is compatible with the voltage of the pump (or you are using an LCB to step down the voltage), you can go as over-sized as you want. There is a law of diminishing returns, which as far as I've heard maxes out at with an array about 150% of the watt requirements of the pump.
Getting back to your question about the Kaneka, one 60 watt panel is not enough power for the pump. Would two panels work? That is still not enough IF one calculates the watt needs of the pump based on the highest current it could draw. What if one uses the lowest current it might draw? Then the pump wouldn't need as much power, right? That is correct, and I have three thoughts on that: first, it is a generally established practice in the industry to size PV systems conservatively. Since we are dealing with a variable resource, since clouds can cross the sky and obscure light at inconvenient times, it's always better to have too much PV rather than not enough.
In your case, you have 20-30 feet of lift and an undetermined requirement for flow rate. Is the lift closer to 20 or 30 feet? The higher the lift, the lower the flow rate. Without knowing exactly what you want the pump to do, it's better to size the array to the maximum performance of the pump, which will maximize your chances of being happy with the system. Another thought is that we don't have a lot of experience with the Shurflo pumps. We have charts and math, but not a lot real world experience. I will be performing a series of labs in the coming weeks with the Kyocera 65, 85, and 135 watt panels and the Shurflo pump noted above, so stay tuned for the results.
The final thought I have is that you can do your own experiment and see what happens. Since Kaneka panels use thinfilm technology, you will definitely need to get an LCB, or linear current booster. LCBs manipulate voltage and current to maximize the performance of the system. In the case of 2 Kanekas and a 12 volt pump, the LCB would step down the voltage from the 48 voltage array to the 12 V pump. In doing so, it would boost the current of the panels. I'm confident that with two Kaneka solar panels and an LCB, the pump would move a fair amount of water. But how much and under what conditions? Your best bet is to see for yourself, or use a conservatively sized array that you know will work.
For an LCB that would work with two Kaneka solar panels, look here:
http://www.altestore.com/store/Solar-Water-Pumps/Linear-Current-Boosters-For-Pumps/Solar-Converters-Ppt-48-10A-48V-Linear-Current-Booster/p1360/If you have any further questions, please let me know.
Sincerely,
Bramley
Technical Sales
altE Store