Many thanks guys! Back to the drawing board.
There is clearly something I’m missing here since if I use the AltE wiring sizing calculator, it gives me only a 1.32mm2 cable, for which the next size up is a 14 gauge which 2.08mm2. Way too small.
Using the calculator formula, a 2 ft cable, running 44A at 24V, with a 3% voltage drop equates to (2 * 44)/(3 * 24) which is for sure a VDI of 1.22. From the table, or using VDI * 1.1, that is a 1.34mm2 cable.
Looking at the Outback controller manual wire run tables, a #8 gives me 6 feet of run at 50 amps. This table gives much larger sizes than the AltE calculator.
What I’m trying to get at here is just what is the calculation for wire sizing then, since you guys are going much bigger than the Outback tables or the AltE calculator.
Let me know your thoughts,
Cheers
Guyanapete
My thoughts are these. Solar panels use way to small of bus wires when the savings is so negligible considering all the other components in the system. Electrical engineers are are far to accustomed to using voltage dropped wire heating guage sizes which aren't really applicable in solar engineering.
Here's a good table.
http://www.powerstream.com/Wire_Size.htmDoubling the thickness of all bus tabbings on your panels would increase throughput significantly only cost a few dollars and make no difference in thickness or ease of production or anything. Everyone needs to pressure solar panel makers to go thicker on cell tabbings.
As for interconnects. Try for .1 max volt drop for every run. If you can save money by not doing that make sure the savings are significant. Pure copper wire is a pain to work with so many manufactures alloy a bit because copper always work hardens IMMEDIATELY. If you take the precious metals you get this.
Copper- Work hardens completely. Hard to work with and you will almost never see it in it's pure state because of this.
Silver- Work hardens middle of the road. Have to work with it a bit to get it to work harden.
Gold- Will not work harden. You can pound it and pound it and pound it and work it into THREADS. It just won't work harden at triple 9 purity.
So good to know exactly what the wire is and make a few small adjustments and try to avoid using voltage drop formulas in solar applications, or understand that it will turn your wires into heating elements.