Proposed PV Installation with Sharp or Sanyo modules:
Tracker: Wattsun AZ-225 Tracker
Controller: Outback MX60 or FLEXmax 80
Combiner Box: Outback Pspv
Wire Run: 45m (150 feet)!
Inverter: Xantrex SW3048E
Battery Bank: 48 volts
I feel confused about Voc, Vpm, Ipm, Isc and nominal voltages when determining wire size. Are the following calculations correct with regards to the array strings and wire sizing?
Would all or any of these arrangements be suitable for an Outback MX60 or FLEXmax 80 and which would you advise in this case? If it's the FLEXmax 80 then why?
The Wattsun AZ-225 Tracker can mount 16 Sanyos and 16 Sharps but is this the only way you can arrange these modules to work with an Outback MX60 or FLEXmax 80?
Modules: 16, Sharp NT-175U1, 175 W STC, 35.4 Vpm, 4.95A Ipm, 44.4 Voc, 5.4A Isc
Array: Eight 2-module series string, 2,800 W STC total, 70.8Vmp
Wire Size: (150 x 39.6) / (2% x 70.
x 1.1 = 46.15mm2, requires #0 AWG!
Modules: 15, Sharp NT-175U1, 175 W STC, 35.4 Vpm, 4.95A Ipm, 44.4 Voc, 5.4A Isc
Array: Five 3-module series string, 2,625 W STC total, 106.2 Vmp
Wire Size: (150 x 24.75) / (2% x 106.2) x 1.1 = 19.23mm2, requires #4 AWG
Modules: 16, Sanyo HIP-180BA3, 180 W STC, 54 Vpm, 3.33A Ipm, 66.4 Voc, 3.65A Isc
Array: Eight 2-module series string, 2,880 W STC total, 108 Vmp
Wire Size: (150 x 26.64) / (2% x 108) x 1.1 = 20.35mm2, requires #4 AWG
Modules: 16, Sanyo HIP-190BA3, 190 W STC, 54.8Vpm, 3.5A Ipm, 67.5 Voc, 3.8A Isc
Array: Eight 2-module series string, 3,040 W STC total, 109.6Vmp
Wire Size: (150 x 28) / (2% x 109.6) x 1.1 = 21.08mm2, requires #2 AWG! or 25mm2 metric
Modules: 16, Sanyo HIP-200BA3, 200 W STC, 55.8 Vpm, 3.6A Ipm, 68.7 Voc, 3.8A Isc
Array: Eight 2-module series string, 3,200 W STC total, 111.6 Vmp
Wire Size: (150 x 28.
/ (2% x 111.6) x 1.1 = 21.29mm2, requires #2 AWG! or 25mm2 metric
How many and what size DC breakers would be required with the Outback Pspv combiner box with these different string sizes?
Also after searching the Internet I don't seam to be able to find many suppliers for PVC insulated 2 core shielded direct burial cable except here
www.grainger.com. Any suggestions and help much appreciated thanks.