Diversion Loads/Dump Loads

I am an electro-mechanical technician by profession for almost three decades now, so don't really consider myself 'In the Dark' about theory of green energy, but of all the sites I have researched I have not found any that offer technical explanation of hybrid systems that incorporate wind, solar and hydro sources. Specifically, I would like more enlightenment on charge controllers that can accept various power inputs and about diversion loads/dump loads that i see as optional. Why is the latter optional and could they also be implemented with solar water heaters since they appear to be heater elements. Controlled by thermostat or charge controller? Looking for informative sites for A-Z instructions on building off-grid system I can add onto.
 
578 Posts
Nov 20, 2007 11:25 am
Re: Diversion Loads/Dump Loads

i have no a-z instructions for you, but

photovoltaic charge controllers do not require dump loads.

wind controllers usually come with the turbine, but if you have a home-made or other smaller unit, you will need a diversion load controller (morningstar tristar, xantrex c-series) and a diversion load.  the diversion load must be able to handle the power from the source and are often required in duplicate (both controller and dump load) by code in case of failure of one.

hydro is much the same as above with the exception that no hydro comes with controller provieded by manufacturer to my knowledge.  all will require dump load controller and dump load usually in duplicate for safety.  these can be resistive loads to air, or to water for heating.

batteries and (off grid) inverters dont care where energy comes from as long as it is regulated and in the paramaters for its proper operation.

james Alt-E staff

AltE
"Making Renewable Do-able"
http://www.altEstore.com/

Tel: 877.878.4060 x107  or +1.978.562.5858 x107
Fax: 877.242.6718  or +1.978.562.5854
 
28 Posts
Nov 20, 2007 02:31 pm
Re: Diversion Loads/Dump Loads

Check out all these articles on the National Renewable Energy Lab site,

http://search.nrel.gov/query.html?col=nrel&qt=hybrid+wind+solar&charset=utf-8&qp=site%3Awww.nrel.gov+site%3Awww.sst.nrel.gov+site%3Arredc.nrel.gov&qc=nrel&ws=0
 
28 Posts
Nov 21, 2007 02:19 pm
Re: Diversion Loads/Dump Loads

Wait a minute.  Did you say that you think diversion loads are optional?  Diversion loads are not optional with hydro or wind.  These devices create electricity from spinning a driver which spins a generator.  Once you have something spinning, its not easy to stop.  If you immediately remove or reduce the braking action (in this case that's the electrical load that they have been ramped up against), they can sometimes take off.... sometimes all the way off.  The diversion load is needed to hold them in place and in one piece, and cool, until they can be ramped back to the new power level output required for the new load.  That's if you have control over the new rpm needed.  Changing the flowrate to a hydro, for example (but you can't change the windspeed so easily).  Until then you have acceleration and a possibility for very high voltages, if the load is ramping down, or brownouts from equipment coming on line, but trying to operate on too low power levels as the load is building, but supply remains relatively low.
 
578 Posts
Nov 21, 2007 03:54 pm
Re: Diversion Loads/Dump Loads

sorry guess that was confusing, when  i said they come with controller, that meant that they have controller and dump load built in like a whisper for example. 

but if you want an example of a wind turbine without a dump load, look no farther than the air x.

james Alt-E staff

AltE
"Making Renewable Do-able"
http://www.altEstore.com/

Tel: 877.878.4060 x107  or +1.978.562.5858 x107
Fax: 877.242.6718  or +1.978.562.5854
 
28 Posts
Nov 22, 2007 01:32 am
Re: Diversion Loads/Dump Loads

I had a look at the AirX cut sheets and they have a speed cotrol that they say kicks in when the batteries have charged and stops the turbine.  When the batteries are charged, apparently the turbine will not start.  That means that, while the batteries are receiving all current, a load "diversion" is not needed as the battery takes 100% of load, and when they are reaching charge, speed control begins and current is limited to less than what can be produced without a diversion load, when charged, breaking kicks in and the stopped turbine (of course) produces nothing and needs no load diversion.  Therefore the AirX turbine does need to accept full load and needs load diversion capability, OR needs speed control while actively spinning.  My previous post above wasn't clear as I did not mention that I was assuming that the case being discussed was limited to fully spinning-free conditions, under which all turbo-machines need load diversion, of which the AirX is no exception.
 
3 Posts
Nov 26, 2007 11:35 pm
Re: Diversion Loads/Dump Loads

Okay, So if I am in understanding, every source of green energy requires its own charge controller and there is not any one that can handle multiple inputs. Any kinetic energy source needs either a braking controller or a method of circumventing excess energy. Still contemplating where excess energy from solar panels goes. Is there an automatic diversion switch that will charge alternate battery bank in leau of dumping (dump as last resort)? I have a plephora of batteries. Thanx to all! 
« Last Edit: Nov 26, 2007 11:48 pm by William Summers »
 
28 Posts
Nov 27, 2007 06:15 am
Re: Diversion Loads/Dump Loads

For efficient use, yes.  A charge controller charges the batteries in a controlled manner, permitting greater current to be sent to the batteries when they are low and reducing the current to the batteries when the charge level comes up.  It isn't a necessity to have charge control, but if not, high currents would be sent to the battery even though they lack only 1 mA from being full.  The idea is that a good portion of those high currents could be used elsewhere whenever the batteries do not need to be charged at full rate.

The Xantrex C Series for example can be used as solar charge controllers or load controllers or load diversion controllers. I haven't been looking closely, so if these aren't, I believe there are multiple input models out there.

I'm not much of an electrical engineer, but as I like to think of it, there are basically two types of generators  used in renewable energy, PV and batteries are one and then the induction type Wind/Hydro generators, which are really just induction motors spinning in reverse.  That's leaving synchronus generators aside.  PVs and Batteries do not derive their voltage from the circuit they are supplying (within limits), whereas induction generators do.  Induction generators need an electric field in which to spin in order to generate their voltage.  The strength of the field is determined by the circuit they are supplying.  Therefore changes in the circuit load, change the field of the generator and consequently change its output.
 

Disclaimer and Disclosure

The Alternative Energy Store, Inc reserves the right, within its sole discretion, to refuse or delete any posting or portion thereof, or terminate or block the access to this forum.

The opinions and statements posted on this forum are the opinions and statements of the person posting same, and do not constitute the opinion or act of the Alternative Energy Store, Inc (AltE). The Alternative Energy Store, Inc does not endorse or subscribe to any particular posting. No posting shall be construed as the act or opinion of the Alternative Energy Store, Inc.

Click here for BBB Business Review

McAfee SECURE sites help keep you safe from identity theft, credit card fraud, spyware, spam, viruses and online scams
Desktop Website | Mobile Website

Share

Click on an icon to share! If you don't see the method you want, hover over the orange "+".

Feedback

What can we do to help you?

Please enter a summary
Sorry, the copyright must be in the template.
Please notify this forum's administrator that this site is using an ILLEGAL copy of SMF!
Copyright removed!!