Re: Converting from AC generator to DC storage or better ideas welcome
"using a 3 X 24amp old AEG generator hooked up to a water turbine"
What do you mean with 3 X 24 amp Generator ? Is that a 3 phase generator with 24 amps per phase ? (What is your generation voltage and how many rpm ?)
If so, how are you keeping the phases balanced, load wise? Part of your problem could be having the majority of the demand on a single phase, at any given time. The generator probably will not produce 24 amps on one phase with minimum draws on the other two.
Running some rough numbers for 80 feet of head and about 120 feet of 14 inch pipe, I get about 750 gpm with the 2 inch nozzle and about 6100 watts. With the 1.5 nozzle, that drops to about 400gpm and 3200watts.
A new single phase alternator would solve the imbalanced 3-phase problem, but you will still be limited to what you can generate with a 2 inch nozzle, or about 6100 watts.
My guess is that your system was originally designed for a larger use. Something on the order of a 3.4 inch nozzle at about 2000 gpm.
Anyway, 3.2kw would give you up to 76.8kWh a day if everything was constant. My guess is that your system runs at a constant water flow, and then the excitation is varied to produce the power required. If that is the case, you may have a lot of un-used generation during periods of low demand. So adding batteries and an inverter could store this unused power, for periods that it is needed, with or without PV.
As far as measuring your generation, a power monitor would do it. Or, a watt hour meter like the one on a house. You might need three, if they are single phase and you are generating 3-phase.