Gordon:
Here is an article for you on the life and death of batteries.
http://www.mpoweruk.com/life.htmTake a look at the section and chart about halfway down, on depth of discharge.
While you may only be getting two hours of full sun now, this summer you should be getting something around 4.5 hours. With your current panels, it is about 6KWh or 125Ah a day. When you increase the panels, it will be closer to 9KWh or 189Ah a day.
189Ah would equate to a 50% DOD on the 37AH bank of eight batteries.
I would give serious consideration to increasing your bank size to 16, and limiting the depth of discharge to about 25%. If you cut your daily draw in the winter to something close to your generation, you would be running less than 10% DOD during winter. That should more than double the life of your batteries. (Talking about the life of the L-16’s, not your previous batteries)
As far as which battery to purchase, I have had good service with both. Interstate makes a good battery, but I believe the Trojans are a little better, and give a longer life in identical service.
I glanced at the info Dave supplied, and question the 3300 cycle life for “Interstates” vs 2800 for the Trojans. We cannot safely assume that the US battery L-16 listed and the Interstate L-16 are identical. I would also look at the warrantee. USB 1 year, Trojan 7 years (I believe that is 3 years free, and prorated to 7).
If it were me, I would go talk to the Trojan dealer and see what type of deal he would be willing to make for me on a bank of 16 batteries. If you are going with eight, you might as well go with the Interstate and put the “saved” 55 dollars towards your next battery purchase.
Ken