Multiple Solar Panel String Scenario

I am curious about the effects of combining multiple strings of solar panels into a combiner box that have different voltages and amperage.   I am assuming this is bad right?  What are the effects?  Would a separate charge controller/cable run be required?

Thank you.

Parker Jardine
 
578 Posts
Oct 3, 2007 05:44 pm
Re: Multiple Solar Panel String Scenario

different voltages, no good. different voltages in series string and or combiner box are a no no.  assuming same nominal voltage, strings of different amperages in a combiner are okay.  the current is just additive on the busbars for the output wiring.

if you have a specific example, let the cat out of the bag.  As soon as i/we get a free sec, someone will answer.

james - Alt-E staff

AltE
"Making Renewable Do-able"
http://www.altEstore.com/

Tel: 877.878.4060 x107  or +1.978.562.5858 x107
Fax: 877.242.6718  or +1.978.562.5854
 
5 Posts
Oct 4, 2007 01:25 pm
Re: Multiple Solar Panel String Scenario

Ok, I have two sunwise OEM40 solar panels that I purchased a few years back.  Recently for a project, I contructed two of my own solar panels with a nominal voltage 0f 16.5 volts.  I want to combine the two strings into a parallel connection in my pspv combiner box.  However, I know this is not recommend, but what are the effects?  One string lowers the voltage of the other string?  What if a person purchases a set of solar panels, and then in the future he or she wants to buy more, but the voltages dont match with the new panels? Either because of manufacuring changes or product discontinuation?
 
578 Posts
Oct 4, 2007 05:28 pm
Re: Multiple Solar Panel String Scenario

hey,

16,5 nominal or 16.5 vmp?  nominal voltage describes the battery bank that you intend to charge (without getting into further detail)

how many cells are in your homebrew modules?  if 36, then you have a 12v module that runs at 16 or 17v.  if around 54, then you have about an 18v nominal module that runs at vmp of 23v or so.

so what if a person purchases modules, and then decides to add more modules later of a different voltage?  hopefully they would think about that before they buy, because that forces them at least to a different charge controller and perhaps a different combiner as well.

james - Alt-E staff

AltE
"Making Renewable Do-able"
http://www.altEstore.com/

Tel: 877.878.4060 x107  or +1.978.562.5858 x107
Fax: 877.242.6718  or +1.978.562.5854
 
5 Posts
Oct 4, 2007 05:58 pm
Re: Multiple Solar Panel String Scenario

I have 30 cells in each module.  So approx 16.5vmp.  Ok, so I should use a different combiner box, and or charge controller.  But lets pretend that I combined them together.  What really would happen?  It sounds like if someone could solve this problem, they could strike it rich.  Because in 10 years, when we all want to add more panels to our system, are we really going to be able to buy the same panels?  Thank you for your help.

-Parker
 
578 Posts
Oct 4, 2007 07:17 pm
Re: Multiple Solar Panel String Scenario

well, no.  if running at 16.5 vmp, and 20 something open circuit then the modules are likely close enough to run to the same charge controller and combine as well.

the issue is that you do not want mixed modules on a pwm controller because higher voltages will blow it up.  anything higher than 28 to 30 will destroy a simple 12v controller.

if you mix module voltages (strings) [or any different modules for that matter] on an mppt controller, the controller will see different IV curves and the max power point tracking will be rendered ineffective.

yes it is a bummer if you try to add to an array and your modules are not around anymore, but i dont see it as big a deal as you do.

as the need to add happens, you add more production. if the same components are around, great, if not you must have a controller to deal with the new solar.  multiple streams feeding the same lake.  no big deal; especially even the most expensive controller is worth less than 200watts.

james - Alt-E staff

AltE
"Making Renewable Do-able"
http://www.altEstore.com/

Tel: 877.878.4060 x107  or +1.978.562.5858 x107
Fax: 877.242.6718  or +1.978.562.5854
 

Disclaimer and Disclosure

The Alternative Energy Store, Inc reserves the right, within its sole discretion, to refuse or delete any posting or portion thereof, or terminate or block the access to this forum.

The opinions and statements posted on this forum are the opinions and statements of the person posting same, and do not constitute the opinion or act of the Alternative Energy Store, Inc (AltE). The Alternative Energy Store, Inc does not endorse or subscribe to any particular posting. No posting shall be construed as the act or opinion of the Alternative Energy Store, Inc.

Click here for BBB Business Review

McAfee SECURE sites help keep you safe from identity theft, credit card fraud, spyware, spam, viruses and online scams
Desktop Website | Mobile Website

Share

Click on an icon to share! If you don't see the method you want, hover over the orange "+".

Feedback

What can we do to help you?

Please enter a summary
Sorry, the copyright must be in the template.
Please notify this forum's administrator that this site is using an ILLEGAL copy of SMF!
Copyright removed!!