� hi john,
"Now what if I put 9 panels in a single string. 43V x 9 = 387Vdc. Thats really high but in tolerance. 34.6 x 9 = 315Vdc thats within the Mpp range of 139-400Vdc. I really dont like the 400 volts DC. Seems awfully lethal to me."
we have to back up a bit here. as much as we want to get the most out of the equipment we have in hand, we just can't get away with a string of more than seven of those 100watt pw1000's
lets go back over to that SMA sizing chart james linked us to.
http://www.sma-america.com/en_US/service/solar-design-tools.html when we put your data in (assuming the sb1800u & swr1800u are one and the same)not knowing your exact jersey location i went with atlantic city new jersey. record low is -23*f (1942) and average high is 85*f (july). the closest choices are..� -22* and 86*f.
the sizing tool gives us 1 string of 5 in series, one string of 6 in series or 1 string of 7 in series,
or 2 strings of 5, of 6 or of 7 in series.
mr. cormican has given some valid reasons to avoid the 2 series strings of 5 and i might trust his judgement on that.
that leaves us with the 6 or 7 string option.
the reason we can't go with more modules in the series string is just as voltage drops in the higher temps the voltage increases in the lower temps. these higher voltages can (will) be destructive to our inverter, not just stopping production as the high temps will.
i sure like that idea of picking up a sb700u to make use of those 4 extra modules (6 on the 1800 & 4 on the 700)
or that other option of 2 more photowatt modules to make up a 2 string array of 6 in series.
keep at it..good to get everything worked out first.
kind regards, dave