http://photovoltaics.sandia.gov/docs/PDF/fieldinvest.pdfIn an ideal world, all things being equal budgetwise, and always rounding up, I would take the watthour load estimated over a 24 hour period and convert it into amphours at a nominal voltage.
Then multiply that by at least 5 to get the size battery bank needed. Then I would take that same watthour estimate and divide it by - the number of hours of equivalent full rated charge per day - with a given PV array orientation for a given region on the shortest day of the year. This may seem bare bones to some but glutonus to others. To each their own.
Example:
Estimated load - 4,000 watthours or 4 kW h's over 24 hour day/night cycle. 24 volts nominal system.
4000/24x5= 833 amphours @ 20 hour rate minimum battery bank.
(I might would go up to a 1200 amphours bank for future use and/or more days of autonomy.
2 hours of equivalent full rated charge from a PV module.
4000/2= 2000 watt PV array
(I might even double this. A lot would depend on site specifics.) The idea of course is to replace what was taken from the batteries as soon as possible.
Undoubtedly though, budget restraints can and will come into play for a lot of people, including myself. Personally, I am disappointed with the PV industry and its pricing. I had expected better prices as PV become more main stream. Oh well, I guess that was just a pipe dream.