Hi again, Janet. I did not mean to imply that you have a short circuit condition in your refrigerator load, but merely that it may appear as a short circuit to your inverter. I don't know what inverter you have, so I can't make a judgement there. When a refrigerant compressor first starts up, it draws an enormous load current, and the inverter may interpret this as a short circuit condition. I would be hesitant to say that you have insufficient battery capacity, but more likely, an insufficient inverter surge capability. In my case, I am running a 48v system as well, with 6 x 16 6v batteries, each with a capacity of 375 amp/hours, and inverter capacity of 11,000 watts, but this means nothing when I try to start up a heat pump compressor that draws a starting current in excess of 55 amps (off scale on my AC ammeter). The inverters just go into fault mode and shut down due to excessive surge current. My solution was to operate the heat pump on its own dedicated line from utility power, and removed it as an inverter load. My refrigerator is an older model (not high efficiency) and runs fine off the inverters. This may or may not have anything to do with the problem you are having, but its my 2 cents worth anyway.
Best wishes with your RE system. Jon C.