Feeding oil burner with SHW

Posted by Jeffrey Guevara on May 12, 2009, 09:06:15 AM

Feeding oil burner with SHW
Does anyone know if this is possible? Would the oil burner realize that the feed water entering the inlet is preheated? Would this cause any issues?

Does anyone know how to size SHW for space heat?

Regards, JWG
 

Posted by Thomas Allen Schmidt on May 15, 2009, 02:55:16 PM

Re: Feeding oil burner with SHW (Reply #1)
Where you say "oil burner" I assume that is a fuel oil burning water heater and if it is like most all other water heaters it is controlled by a temperature switch. If so then all it "knows" is if the water is at a preset low temperature it "calls" for heat and when it reaches a preset high temperature it turns the heat source off. If the water coming in from a solar water heater is in between those preset temperatures it will not "call" for more heat and if it does, the amount time the heat is on, is shorter as determined by the incoming water temperature. Although some solar water heaters can reach extremes of their own if not regulated. I have seen simple flat plate solar water heaters reach temperatures of 180 degrees Fahrenheit, where as most domestic water heaters are set to a high limit of 120 degrees Fahrenheit with safety temperature/pressure vales that "blow" at 150 degrees Fahrenheit or, I think its, 200 pounds per square inch which ever comes first. 
http://store.altestore.com/Solar-Water-Heaters/c402/
If this doesn't do it for you there is also -
http://www.kingsolar.com/
and - http://www.radiantcompany.com/ - and - http://www.warmair.com/html/hydro-air.htm - or - well, I think you get the idea.
 

Posted by Jeffrey Guevara on May 18, 2009, 07:01:01 PM

Re: Feeding oil burner with SHW (Reply #2)
Well thanks for the response Thomas. Now I know that it is possible. Now the question is, how much potable water do I need to create to effectively preheat an oil fired water heater sized at 150,000 BTU. Any tips on this?

JWG
 

Posted by Arthur T on June 21, 2009, 01:41:02 AM

Re: Feeding oil burner with SHW (Reply #3)
Insufficient data...   However remember that 1 BTU is the amount of heat needed to raise 1 pound of water 1 degree F.  Therefore you have to figure how many degrees of temperature difference you need between your incoming water feed and the desired temp. going into the boiler, and divide that into the 150kBTU number.  This will tell you how many pounds of water, which when divided by the weight of the water (approx 8 lbs / gallon) will then give you the number of gallons needed.

It might be helpful if you could give more details about what you are trying to accomplish - is this a DHW heater?  Are you simply trying to prevent it from burning oil?

A couple of other things to consider -

1. If you EVER get freezing temps in your location, you MUST have some sort of freeze protection in the solar system - either by using a drain-back type setup, or using a seperate loop w/ a glycol antifreeze mix and a heat exchanger in the tank.  The latter is probably more efficient as it will need less energy to circulate the heated water. 

2. It is probably better to have a tank that you heat with a seperate heat exchanger fed by a panel with its own fluid circulation system.  This will get the heat from your roof into the system much more efficiently than trying to run your cold feed through the panel as needed to replenish the hot water supply as it is used.  It also allows a relatively low output panel to supply heat over a long period of time rather than attempting to instantly heat water as it is being used.

3. Often it is good to "overheat" the water in the storage tank, as this greatly increases your effective supply volume.  Standard DHW systems run at around 120*F, and codes say that you should NEVER get hotter than that out of the faucets to avoid scalding dangers. 

The way to do this is set up your tank to let it get heated up to 180-190*F if the panel will push it that hard, and then use an automatic "mixing valve" on the tank output to mix whatever temperature is in the tank w/ added cold water to bring it back to 120*F. 

Set the oil burner to fire at 120*F, so as to maintain your guaranteed minimum temperature in the tank.  If the solar can get the tank to, or above that temp, it will keep the burner from firing at all, if not, the burner will fire less as it only has to make up the difference between what the solar does and the set temperature.

ART
 
Forums | Design by Scratchmedia | Development by SMF.
© 2001-2005, Lewis Media. All Rights Reserved.

Disclaimer and Disclosure

The Alternative Energy Store, Inc reserves the right, within its sole discretion, to refuse or delete any posting or portion thereof, or terminate or block the access to this forum.

The opinions and statements posted on this forum are the opinions and statements of the person posting same, and do not constitute the opinion or act of the Alternative Energy Store, Inc (AltE). The Alternative Energy Store, Inc does not endorse or subscribe to any particular posting. No posting shall be construed as the act or opinion of the Alternative Energy Store, Inc.

 