breaker & fuse sizing for panels

73 Posts
May 18, 2008 06:18 pm
breaker & fuse sizing for panels

Hello,

New to this forum and just ordered the  Photovoltaics: Design & Install Manual. While I'm waiting for it's arrival, can someone help me understand how to size the breakers for the PV  and the fuse size for coming off the battery bank to the inverter? Do I even have the location of these items figured correctly? If not, please impart some wisdom my way.

Thanks
James
 
73 Posts
May 25, 2008 02:49 pm
Re: breaker & fuse sizing for panels

Ha!  the book answered my question perfectly...

J
 
578 Posts
May 25, 2008 02:59 pm
Re: breaker & fuse sizing for panels

breakers for combiner are 1.56 times series string isc or the max series fuse size listed on the module.

total array disconnect (before charge controller) is total array isc times 1.56

inverter to battery disconnect is found in 690.8.

continuous power divided by lowest dc operating voltage times inverter efficiency

hope that helps, write back if need be

james on location in chicago
Alt-E staff

AltE
"Making Renewable Do-able"
http://www.altEstore.com/

Tel: 877.878.4060 x107  or +1.978.562.5858 x107
Fax: 877.242.6718  or +1.978.562.5854
 

Disclaimer and Disclosure

The Alternative Energy Store, Inc reserves the right, within its sole discretion, to refuse or delete any posting or portion thereof, or terminate or block the access to this forum.

The opinions and statements posted on this forum are the opinions and statements of the person posting same, and do not constitute the opinion or act of the Alternative Energy Store, Inc (AltE). The Alternative Energy Store, Inc does not endorse or subscribe to any particular posting. No posting shall be construed as the act or opinion of the Alternative Energy Store, Inc.

Click here for BBB Business Review

McAfee SECURE sites help keep you safe from identity theft, credit card fraud, spyware, spam, viruses and online scams
Desktop Website | Mobile Website

Share

Click on an icon to share! If you don't see the method you want, hover over the orange "+".

Feedback

What can we do to help you?

Please enter a summary
Sorry, the copyright must be in the template.
Please notify this forum's administrator that this site is using an ILLEGAL copy of SMF!
Copyright removed!!