When would you use 12v, 24v, 48v, or 96v batteries for an off-grid system? Is it strictly cost related or is there an advantage of one over the next?
 
163 Posts
Mar 13, 2009 12:39 pm
Re: Batteries / Off-Grid

When would you use 12v, 24v, 48v, or 96v batteries for an off-grid system? Is it strictly cost related or is there an advantage of one over the next?

Say for example you plan to use a 3600 watt inverter to provide 120V a/c power. The current from your batteries to the inverter with a 12V system would be 3600/12 or 300A. With a 24V system it would be 150A, and with a 48V system it would be 75A etc.

With a 12V system you will need larger more expensive battery cables with higher ampacity and larger more expensive breakers. If on the other hand, you plan to run DC powered appliances direct from the batteries then you will find a far greater selection of 12V appliances than you will at higher voltages.

I tend to go with higher voltages which means lower currents, less losses, and the ability to use smaller and cheaper (also easier to work with) cables and breakers.
 
19 Posts
Mar 19, 2009 02:59 pm
Re: Batteries / Off-Grid

Andrew,

Selecting battery voltage is often a matter of finding the meeting point of several variables, including: inverter needs (W continuous and surge), charge controller needs (itself a function of dc source input and battery bank), and available/affordable batteries with which to build your battery bank.

Which variable above is most important in your situation will probably become the dominant determining factor. But in general, the larger the inverter (in W continuous capacity), the higher your battery bank voltage will need to be. E.g., 12V inverter options become quite limited above about 2500W output capacity; that's mostly due to the increased amperage that you have to handle (in your cabling and over-current protection devices).

I might suggest our articles on batteries (as well as others in our Library):

http://howto.altestore.com/Library-Articles/Solar-Electric-Power-or-PV-Systems/Batteries/c19/

~Ben
altE
 
19 Posts
Apr 26, 2009 11:05 am
Re: Batteries / Off-Grid

12v is generally for short runs, small setups, low total wattage, and/or the direct running of 12v devices.  Once you start looking at running a household on PV, it becomes more prudent to step up to 24v or 48v for the panels and battery bank, and then bump the output to regular 120v/240v through the inverter and use normal (albeit 'energy star' or energy miserly) devices and wiring throughout the house.

As for 96v.... why?  Even if you have 72v panels it is no problem to simply bump them down to charge a 48v battery bank via the controller.  Not much PV equipment is made for 96v setups....as 48v is about the upper limit for most off-the-shelf PV equipment.
 
578 Posts
Apr 26, 2009 03:44 pm
Re: Batteries / Off-Grid

off grid equipment is generally not found above 48v nominal because of this:

nec 690.71b

storage batteries for dwellings shall have cells connected so as to operate at less than 50 volts nominal.

--

as regards to controllers down converting from 72v, that is true, but in most cases not 72v nominal, where 690.7 cold temp deration in colder climates will prevent 72v nominal pv input to most mppt controllers that have max vdc of 150.  48 and 60v nominal array inputs are fairly common though.

enjoy the sunny weekend,

james
altE staff

AltE
"Making Renewable Do-able"
http://www.altEstore.com/

Tel: 877.878.4060 x107  or +1.978.562.5858 x107
Fax: 877.242.6718  or +1.978.562.5854
 
Apr 26, 2009 07:34 pm
Re: Batteries / Off-Grid

Higher DC voltages (typically 80 or more but not limited to that) have a tendency of grabbing a hold of a victim and not letting go of them if they get caught in the flow and, not just pos. to neg. where the victim is the "load." But also if the victim gets in series with neg. to neg. or pos. to pos. in a closed circuit or another way of saying that, while a load is present. Actually, it locks up the victims muscles so they can't let go. At the risk of sounding morbid, have you ever seen what happens to a hotdog overcooked? Just ask Samuel W. Smith. Uuh, have you got a Ouija board? I just want you to know what your working with. The worst thing that can happen is that we get "cavalier" about working with electricity.� 
http://organizedwisdom.com/Electrical_Shock_Deaths
This is only one reason for NEC 690.71b
http://ebsco.smartimagebase.com/generateexhibit.php?ID=719
It happens to somebody everday.
Don't be "somebody."
Be sure all of the tools you use to work on live circuits such as batteries and exposed PV modules and arrays are completely insulated from conducting electricity. Know what all of the electrical potentials are around you at all times. Don't assume a circuit is off, check with an appropriate test meter. Also be aware that flooded cell lead acid batteries can "blow" acid under certain circumstances. Wear the appropriate protective gear when working with batteries.
« Last Edit: Apr 26, 2009 07:39 pm by Thomas Allen Schmidt »
 
19 Posts
Apr 27, 2009 04:56 pm
Re: Batteries / Off-Grid

off grid equipment is generally not found above 48v nominal because of this:

nec 690.71b

storage batteries for dwellings shall have cells connected so as to operate at less than 50 volts nominal.

--

as regards to controllers down converting from 72v, that is true, but in most cases not 72v nominal, where 690.7 cold temp deration in colder climates will prevent 72v nominal pv input to most mppt controllers that have max vdc of 150.  48 and 60v nominal array inputs are fairly common though.

enjoy the sunny weekend,

james
altE staff

Huh?  "Cold temp derating" would mean that 72v panels would be putting out less than their normal rated voltage, not more.  For instance, I've got a 40watt 72v panel that puts out upwards of 90v on a nice sunny day.  So to use that panel to charge a 48v battery bank I would simply need to pair it with a charge controller that was rated to handle the max voltage (90v+) that the panel was capable of putting out.  Sure, there's some 'loss' reducing from 72v to a 48v battery bank, but the good news is that even if the panels are extremely dirty they'd still be putting out more than the 48v necessary to charge the battery bank.  As an example, I can partially shade the panel and it still puts out between 50v-60v, perfect for a 48v battery bank.
 
578 Posts
Apr 27, 2009 05:23 pm
Re: Batteries / Off-Grid

you bring up a good point.  perhaps i was unclear.  nec 690.7 provides multiplication factors in addition to VOC for poly and monocrystalline modules.  so by taking this factor, the voltage as it pertains to the code and other equipment would be higher.

on the subject of language, you mention 72v panel.  for clarity do you mean "panel" as
a. 1 photovoltaic module
or
b. 2 or more photovoltaic modules wired in series; commonly referred to as a series string, but described in the code as a panel (figure 690.1a)

operating under the assumption of "a", i would assume that the module in your example is a thin film silicon type, or perhaps other type of thin film.  if i had to guess i would say bp millenia.  that being said, if it had a vmp at either 70 or 90v, you are right, even in cold temps, it would likely not make it over the 150v damage threshold of many modern mppt controllers. also, 690.7 would not apply, and you would use the manufacturer's given temp coefficient of voltage to calculate max cold temp VOC.  If  i guessed right and it is the millenia or other thin film module, if you have more than one of those modules, they would all be wired in parallel to prevent the over-voltage (150) that you dont want going to your controller. 

i misused the term derate for 690.7, as it implies lower.  the voltage is not lower, but it corrects voltage higher, thus limiting number of modules per series string in mppt sizing.  that is why i refer to it as derating, lowering the available high end string possibilities.

thanks for participating in the forum, and helping me keep my terminology clear.

james
altE staff

AltE
"Making Renewable Do-able"
http://www.altEstore.com/

Tel: 877.878.4060 x107  or +1.978.562.5858 x107
Fax: 877.242.6718  or +1.978.562.5854
 
19 Posts
Apr 27, 2009 07:59 pm
Re: Batteries / Off-Grid

Thanks for the clarification.  Correct, its a single panel of the thin film variety, a BP/Solarex Millennia as you state.
 

Disclaimer and Disclosure

The Alternative Energy Store, Inc reserves the right, within its sole discretion, to refuse or delete any posting or portion thereof, or terminate or block the access to this forum.

The opinions and statements posted on this forum are the opinions and statements of the person posting same, and do not constitute the opinion or act of the Alternative Energy Store, Inc (AltE). The Alternative Energy Store, Inc does not endorse or subscribe to any particular posting. No posting shall be construed as the act or opinion of the Alternative Energy Store, Inc.

Click here for BBB Business Review

McAfee SECURE sites help keep you safe from identity theft, credit card fraud, spyware, spam, viruses and online scams
Desktop Website | Mobile Website

Share

Click on an icon to share! If you don't see the method you want, hover over the orange "+".

Feedback

What can we do to help you?

Please enter a summary
Sorry, the copyright must be in the template.
Please notify this forum's administrator that this site is using an ILLEGAL copy of SMF!
Copyright removed!!