Hi I'm wondering is there any real benefit of having a battery bank larger than a 12 volt system. With the MPPT controllers allowing a higher voltage input (allowing a smaller diameter wire run) do I really need to step up to a 24/48 system. As we all know inverters are not cheap. I am building a system for my retirement home out of the country, and am adding a new component on every year. My fridge is 12 volt and I am at the point where I need to get a pump for water pressure and a Air X Marine wind generator. So is 12 volt good or do I need to get a transformer for my fridge and upgrade to a 24/48 inverter, Thanks
 
Jun 2, 2008 05:16 am
Re: 12 volt system

We face a simalar question with industrial electric motor applications, 120/208, 120/240, or 277/480, only we are limited most of the time to whatever grid service is allready in place.

Unless I was expecting loads with potentially high amperages and/or loads with potentially long wire runs, I would use 12 volts nominal.
If I were planning to have all 120/240 vac loads from an inverter(s), then I would consider a higher nominal battery voltage.
Two - 4000 watt inverters for example have the potential for 8000 watts of load. At 12 volts nominal that would be 667 amps, at 24 - 333, and at 48 - 167. Obviously these numbers would get cut in half for each of the two inverters, if I were using a two pole fused disconnect between them and the battery.
If so, I could use a 100 amp disco. @ 48 nominal, 200 amp disco. @ 24, but at 12 volts nominal I would need a 400 amp disconnect. Not only would this last one be expensive but they are about as big a fridge.
 And I haven't even gotten into wire sizing for these examples. In all actuality the wire sizing should be done with the inverter(s) highest surge watt rating at vac and its low voltage dc cut off set point.
Have you ever seen a water hose with a whole lot of pressure and volume of water coming out and no one holding it? Wire will do the same thing when there is more amps on it than its size is rated for plus it could catch itself and other things around it on fire. www.nfpa.org

Of course there is no way that I could fully know what all of your loads are, so I am just making up examples.
 Such as, lighting loads at the nominal battery voltage. A 100 watt incandescent bulb at 12 volt nominal will draw 8 amps, so at best you could get 2 of them per 20 amp circuit on awg #12 wire. Chances are, in a conventional built home, the length of the wire for that circuit and the lower voltage would make it necessary to put only one 100 watt bulb on that circuit due to power loss. With two there would be light but not as brite.

Its all a little like building a car. You have to know what you going to do with it first, a commuter or an eliminator, then you can build it.
http://www.kronosport.com/
versus
http://www.nedra.com/

I would go on but its time for work. There seems to be no end to trouble shooting problems with industrial motor controls and motors.
 

Disclaimer and Disclosure

The Alternative Energy Store, Inc reserves the right, within its sole discretion, to refuse or delete any posting or portion thereof, or terminate or block the access to this forum.

The opinions and statements posted on this forum are the opinions and statements of the person posting same, and do not constitute the opinion or act of the Alternative Energy Store, Inc (AltE). The Alternative Energy Store, Inc does not endorse or subscribe to any particular posting. No posting shall be construed as the act or opinion of the Alternative Energy Store, Inc.

Click here for BBB Business Review

McAfee SECURE sites help keep you safe from identity theft, credit card fraud, spyware, spam, viruses and online scams
Desktop Website | Mobile Website

Share

Click on an icon to share! If you don't see the method you want, hover over the orange "+".

Feedback

What can we do to help you?

Please enter a summary
Sorry, the copyright must be in the template.
Please notify this forum's administrator that this site is using an ILLEGAL copy of SMF!
Copyright removed!!