Posted by James Cormican on July 27, 2009, 10:26:07 AM

modified sine wave inverters v. afci breakers
has anyone noticed problems with off grid systems in which a properly installed hardwire modified sine wave inverter is tripping afci breakers for bedroom circuits but not affecting the other breakers?

if so please tell, specificity on make and model of inverter and ac panel/breakers appreciated.

james
altE staff

AltE
"Making Renewable Do-able"
http://www.altEstore.com/

Tel: 877.878.4060 x107  or +1.978.562.5858 x107
Fax: 877.242.6718  or +1.978.562.5854
 

Posted by Bruce Friedman on July 27, 2009, 11:13:41 AM

Re: modified sine wave inverters v. afci breakers (Reply #1)
James- are you sure it is related to the inverter....we have problems with the afci breakers all the time in homes with out pv.  They are very sensitive....could be a dimmer, light fixture, etc.

Just my 2 cents...

BF
 

Posted by James Cormican on July 27, 2009, 11:27:25 AM

Re: modified sine wave inverters v. afci breakers (Reply #2)
nope not sure, thanks for the reply.  good point, this is out of my normal realm, so all input is welcome. 

that is from 2002 code, correct?, and most of the country has adapted to it.  so what do you do when you find these issues; is it a wild goose chase to find what the issue is?

james
altE staff

AltE
"Making Renewable Do-able"
http://www.altEstore.com/

Tel: 877.878.4060 x107  or +1.978.562.5858 x107
Fax: 877.242.6718  or +1.978.562.5854
 

Posted by Ken Hall on July 28, 2009, 03:16:22 PM

Re: modified sine wave inverters v. afci breakers (Reply #3)
There are plenty of AFCI problems without an inverter.

"Loose plugs" can cause tripping. Make sure the plug/receptacal fit is tight.
Shared neutrals.
Multiple electronic ballasts. (Too many CFL's would do it)
Surge protectors that have reached the end of life. (MOV leaking excess current to ground)
RF noise

Ken
 

Posted by Robert Dinion on October 02, 2009, 06:40:24 PM

Re: modified sine wave inverters v. afci breakers (Reply #4)
Unfortunately it probably is the inverter tripping the breaker.  The way AFCI circuits work is by detecting the non sinusodal wave forms that occur when arcing occurs.

This article has a really great picture about halfway down that shows this.
http://www.pfeiffereng.com/The%20Arc%20Fault%20Circuit%20Interrupter.pdf

So you either have to go sine wave or replace your outlets.
This is going to be a big problem in some installations so altE needs to drop the price of sine wave inverters. Smiley
« Last Edit: October 02, 2009, 06:52:44 PM by Robert Dinion »
 
Forums | Design by Scratchmedia | Development by SMF.
© 2001-2005, Lewis Media. All Rights Reserved.

Disclaimer and Disclosure

The Alternative Energy Store, Inc reserves the right, within its sole discretion, to refuse or delete any posting or portion thereof, or terminate or block the access to this forum.

The opinions and statements posted on this forum are the opinions and statements of the person posting same, and do not constitute the opinion or act of the Alternative Energy Store, Inc (AltE). The Alternative Energy Store, Inc does not endorse or subscribe to any particular posting. No posting shall be construed as the act or opinion of the Alternative Energy Store, Inc.

Call us for solar panel system design help.
877-878-4060

Se habla Español
 

top members