I have a client for whom we just replaced 30 batteries feeding a UPS system. The UPS takes power from the utility or an inverter for the batteries. The feed into the inverter from the UPS bateries is two legs of DC @ 12 x 15, or roughly 180 VDC per leg, output is 230 VAC into the UPS.

He also has an 8kw manual start, stand-by generator that he may plug into the panel. He uses a manually operated transfer switch, disconnecting the utility feed and engaging theĀ  genset.

Recently, he had someone else install a solar system feeding into the same panel. Therefore, the inverter will almost always be in parallel with another source of power, but only the utility can accommodate a constant full power back-feed from the inverter.

I do not think a standard grid-tie inverter is the right way to go. What inverter will automatically scale back its output so as not to overdrive the genset  or the back up batteries on the UPS(like the demand is only 3 kw, it is the middle of a sunny afternoon, and both the solar and genset and UPS are online)?
« Last Edit: Nov 9, 2008 10:58 am by Gary Fuller »
 

Disclaimer and Disclosure

The Alternative Energy Store, Inc reserves the right, within its sole discretion, to refuse or delete any posting or portion thereof, or terminate or block the access to this forum.

The opinions and statements posted on this forum are the opinions and statements of the person posting same, and do not constitute the opinion or act of the Alternative Energy Store, Inc (AltE). The Alternative Energy Store, Inc does not endorse or subscribe to any particular posting. No posting shall be construed as the act or opinion of the Alternative Energy Store, Inc.

Click here for BBB Business Review

McAfee SECURE sites help keep you safe from identity theft, credit card fraud, spyware, spam, viruses and online scams
Desktop Website | Mobile Website

Share

Click on an icon to share! If you don't see the method you want, hover over the orange "+".

Feedback

What can we do to help you?

Please enter a summary
Sorry, the copyright must be in the template.
Please notify this forum's administrator that this site is using an ILLEGAL copy of SMF!
Copyright removed!!